https://www.hkfsd.gov.hk/eng/source/licensing/FS_Market_eng.pdf
呢份2021年既FSD letter可以參考下, 寫得好詳細, 但當然消防唔批, 你都係要兩層sprinkler
Obstruction to fire service installations
1. False ceiling blocks sprinkler heads thus affecting their thermal
sensitivity and water discharge pattern in case of fire. Rectification
can be done by either removing the whole false ceiling, or
conforming to the relevant FSD Circular Letter by:
(a) installing an additional layer of sprinkler heads below the false
ceiling; or
(b) extending sprinkler heads below the false ceiling, if the
concealed space at ceiling contains no other materials except
those specified and its maximum height is less than:
(i) 800 mm (applicable to system installed in conformity with
Rules of the Fire Offices' Committee for Automatic
Sprinkler Installation or LPC Rules incorporating BS
5306-2); or
(ii) 300 mm (applicable to systems installed in conformity to
FSD Circular Letter No. 5/2020).
3. Ventilation air duct may also affect the coverage of sprinkler heads.
Rectification can be made either by removing/ rearranging the air
duct, or relocating/ adding sprinkler heads. Additional sprinkler
heads shall be installed below the air duct, if the width of air duct is:
(a) more than 800 mm for rectangular duct; or
(b) more than 1000 mm for circular duct.
除左風喉之外, 如果你係做Maintenance platform之類會阻住sprinkler運作既都要加多層sprinkler比佢, 試過要做三層sprinkler